Dear All, I found out the previous discussion However, in my case more into the temperatures in the adjacent rooms. Do you think this is due to the ratio of the compartments? (L/H and W/H)? Or is there any reason for that? Thanks |
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 10 replies
-
|
FDS and CFAST are very different codes. CFAST for example cannot account for the fact that the room 27 doorway is offset in the corner diagonally opposite from where rooms 6 and 8 are. But there are also many differences between your inputs and potential issues with your FDS inputs: -You don't have great grid resolution for the two small room doorways. The 6 door is 2 cells wide and 8 is 3 cells. |
Beta Was this translation helpful? Give feedback.
-
|
I have a curiosity about this statement " CFAST for example cannot account for the fact that the room 27 doorway is offset in the corner diagonally opposite from where rooms 6 and 8 are". Why that is the case? I did not find the answer in the manual for the vent position. Could somebody explain it? Thanks |
Beta Was this translation helpful? Give feedback.



FDS and CFAST are very different codes. CFAST for example cannot account for the fact that the room 27 doorway is offset in the corner diagonally opposite from where rooms 6 and 8 are. But there are also many differences between your inputs and potential issues with your FDS inputs:
-You don't have great grid resolution for the two small room doorways. The 6 door is 2 cells wide and 8 is 3 cells.
-Your door openings are not the same size for CFAST and FDS. For example, in CFAST 6-27 is 0.72 x 1.77 and in FDS on your grid it is 0.53 x 1.82. These are A*H^0.5 of 1.7 and 1.3 which is a fairly significant difference.
-In CFAST th C-Class surface is 1 cm thick and in FDS you have it 6 cm thick…