Where does this table come from? Perhaps there is more explanation given in the reference. My guess is that these ratios represent the range of applicability of the various empirical models used for corridors or shafts. In any event, these values are merely suggestions. You are the one who must determine if a particular assumption in the model is valid for your scenario. Nobody but you (or maybe the authority having jurisdiction) can make the decision. |
Beta Was this translation helpful? Give feedback.
-
|
Length and Width are essentially the same. The difference is about how they orient in space. However, for the table L is the longer dimension and W is the shorter. There are issues with flow down corridors, which can really change early answers. The other issue is as L/W grows the more heat is removed from the compartment via radiation and convection from the layers. The W/H is more about how much heat goes through the ceiling then the walls. Too much energy out the ceiling causes some issues with ceiling jets if I remember correctly. |
Beta Was this translation helpful? Give feedback.
-
|
My mistake. I believe you are correct. Sorry.
From: Jason Floyd ***@***.***>
Sent: Friday, August 15, 2025 9:41 AM
To: firemodels/cfast ***@***.***>
Cc: Reneke, Paul A. (Fed) ***@***.***>; Comment ***@***.***>
Subject: [EXTERNAL] Re: [firemodels/cfast] Query on aspect ratios (Discussion #2207)
I thought W/H < 0.2 meant a shaft like geometry where the issue is the plume fills the plan area and can no longer be considered an unbounded, axisymmetric plume.
-
Reply to this email directly, view it on GitHub<#2207 (reply in thread)>, or unsubscribe<https://github.com/notifications/unsubscribe-auth/ADDV4MDTVUYTATZZ64CGLZL3NXPNRAVCNFSM6AAAAACD7A53XKVHI2DSMVQWIX3LMV43URDJONRXK43TNFXW4Q3PNVWWK3TUHMYTIMJRG4YDIMI>.
You are receiving this because you commented.Message ID: ***@***.******@***.***>>
|
Beta Was this translation helpful? Give feedback.


Uh oh!
There was an error while loading. Please reload this page.
-
Hi, I would like to better understand what these aspect ratios means. Do we have to comply to all these ratios when modelling our cfast model.
Reason being, I have a room on fire, and I intend to have this smoke spill into a common corridor for extraction. The size of the corridor is approximately 15m (L) x 2.2m (W) x 3.6m (H). Under the corridor flow, I am only able to fulfil the criteria of L/W > 5. Where does this bring me next?
Thank you in advance!